Question 13071 of 790 · California General Electrician Exam
A 4 inch by 1-1/2 inch octagonal box (15.5 cu in) will contain a fixture stud, four 14 AWG insulated conductors and one 14 AWG equipment grounding conductor. What volume is required, and does the box comply?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13071
- C: 12.0 cu in, the box complies
Explanation
The fixture stud counts as one conductor, the grounding conductor counts as one and the four insulated conductors count four: 6 x 2.0 = 12.0 cu in. That is less than 15.5 cu in, so the box is large enough.
More questions: Electrical Calculations
- 13072A 3 inch by 2 inch by 3-1/2 inch device box is rated 18.0 cu in. It holds a switch, two 14 AWG cables with grounds (4 insulated conductors) and internal clamps. How many additional 14 AWG insulated conductors may be added?
- 13073A conductor runs unbroken through a box without being spliced or terminated and is not looped. How is it counted for box fill?
- 13074What is the maximum fill percentage for a raceway that contains three or more conductors, other than a short nipple?
- 13075What maximum fill percentage applies when exactly two conductors are installed in a raceway?
- 13076A raceway nipple not exceeding 24 inches long between enclosures may be filled to what percentage?
- 13077Using a 40 % fill area of 0.213 sq in for 3/4 inch EMT and an area of 0.0133 sq in for 12 AWG THHN, how many 12 AWG THHN conductors are permitted?