Correct answer to question 12096
- D: 147.6 kVA
Explanation
12 x 30 kVA = 360 kVA connected. Table 220.84 gives 41 % for 12 to 13 units: 360 x 0.41 = 147.6 kVA. House loads are added using the standard method.