Under the NEC 2020 or 2023, what is the demand load for one 15 kW household range?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12086
- B: 9.2 kW
Explanation
Column C gives 8 kW for one range up to 12 kW; above that it rises 5 % per kW over 12 (Table 220.55, Note 1). 15 kW is 3 kW over, so 8 x 1.15 = 9.2 kW.