Question 10037 of 1003 · California General Electrician Exam
125-volt, single-phase receptacles within what distance of the inside walls of a hydromassage bathtub require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10037
- D: 6 ft
Explanation
All 125-volt, single-phase receptacles not exceeding 30 amperes located within 6 ft of the inside walls of a hydromassage bathtub must be GFCI protected. The tub circuit itself also needs its own readily accessible GFCI.
More questions: Special Equipment, Pools, PV and EV
- 10038For a fountain, which equipment requires GFCI protection unless it is listed for operation at low voltage?
- 10042A pool pump motor is connected to a single-phase, 240-volt, 20-ampere branch circuit. What protection is required for the outlet?
- 10043Branch circuits for wet-niche pool luminaires must contain an insulated copper equipment grounding conductor of at least what size?
- 10044What is the maximum PV system voltage permitted for PV systems on one- and two-family dwellings?
- 10045What is the maximum PV system voltage on or in buildings other than one- and two-family dwellings?
- 10046A PV module has a short-circuit current (Isc) of 10 amperes. Using the standard method, what is the maximum circuit current for that PV circuit?