Question 10043 of 1003 · California General Electrician Exam
Branch circuits for wet-niche pool luminaires must contain an insulated copper equipment grounding conductor of at least what size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10043
- A: 12 AWG
Explanation
Wiring to underwater wet-niche luminaires must include an insulated copper equipment grounding conductor sized per 250.122 but not smaller than 12 AWG. A bare or aluminum EGC is not acceptable in this part of the installation.