Question 10049 of 790 · California General Electrician Exam
Under PV rapid shutdown rules, conductors outside the array boundary must be reduced to no more than what voltage within 30 seconds of initiation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10049
- D: 30 volts
Explanation
Controlled conductors located outside the array boundary must be limited to not more than 30 volts within 30 seconds of rapid shutdown initiation. This protects firefighters working on or near the building.
More questions: Special Equipment, Pools, PV and EV
- 10050For PV rapid shutdown, the array boundary is defined as what distance from the array in all directions?
- 10052For one- and two-family dwellings, where must the PV rapid shutdown initiation device be located?
- 10053A PV system has dc circuits operating at 80 volts or more between any two conductors. What protection is required?
- 10055A PV module has an open-circuit voltage (Voc) of 40 volts. Ten modules are connected in series, and the temperature correction factor for the lowest expected ambient temperature is 1.12. What is the maximum PV circuit voltage?
- 10056A PV module has a temperature-corrected Voc of 48 volts. What is the maximum number of modules that can be connected in series on a one- and two-family dwelling?
- 10064What protection is required for receptacles installed for the connection of EV charging equipment?