Question 10036 of 790 · California General Electrician Exam
How must a hydromassage bathtub be supplied?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10036
- C: On an individual branch circuit protected by a readily accessible GFCI
Explanation
Hydromassage bathtubs and their electrical components must be on an individual branch circuit and protected by a readily accessible GFCI. Receptacles within 6 ft of the tub must be GFCI protected as well.
More questions: Special Equipment, Pools, PV and EV
- 10038For a fountain, which equipment requires GFCI protection unless it is listed for operation at low voltage?
- 10042A pool pump motor is connected to a single-phase, 240-volt, 20-ampere branch circuit. What protection is required for the outlet?
- 10044What is the maximum PV system voltage permitted for PV systems on one- and two-family dwellings?
- 10045What is the maximum PV system voltage on or in buildings other than one- and two-family dwellings?
- 10046A PV module has a short-circuit current (Isc) of 10 amperes. Using the standard method, what is the maximum circuit current for that PV circuit?
- 10047A single PV string has modules with an Isc of 10 amperes. What is the minimum conductor ampacity before adjustment and correction, applying both 125 percent factors?