Question 10007 of 925 · California General Electrician Exam
125-volt, 15- and 20-ampere receptacles installed in elevator pits, hoistways, and on car tops require what protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10007
- A: GFCI protection for personnel
Explanation
Article 620 requires GFCI protection for 125-volt, single-phase, 15- and 20-ampere receptacles in pits, hoistways, on car tops, and in machinery spaces. These areas can be damp and are worked in by maintenance personnel.
More questions: Special Equipment, Pools, PV and EV
- 10008The disconnecting means for crane runway conductors must be of what type?
- 10009When may an information technology equipment room use the special provisions of Article 645?
- 10011Branch-circuit conductors supplying information technology equipment under Article 645 must have an ampacity of not less than what percentage of the total connected load?
- 10012What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
- 10013125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?
- 10014At a dwelling with a permanently installed pool, where must the required 125-volt, 15- or 20-ampere receptacle be located?