Question 10014 of 790 · California General Electrician Exam
At a dwelling with a permanently installed pool, where must the required 125-volt, 15- or 20-ampere receptacle be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10014
- B: Not less than 6 ft and not more than 20 ft from the inside wall, and not more than 6 ft 6 in above grade
Explanation
At dwelling units, at least one 125-volt, 15- or 20-ampere receptacle on a general purpose branch circuit must be placed between 6 ft and 20 ft from the inside wall of the pool. It may not be more than 6 ft 6 in above the floor, platform, or grade.
More questions: Special Equipment, Pools, PV and EV
- 10016Over an outdoor pool, what is the minimum height of a luminaire or ceiling fan above the maximum water level?
- 10017In an indoor pool area, the minimum height for a luminaire over the pool may be reduced to what height if the luminaire is totally enclosed and GFCI protected?
- 10018Switching devices must be located at least how far horizontally from the inside walls of a pool, unless separated by a solid fence, wall, or permanent barrier?
- 10020Unless listed for a lesser depth, the top of the lens of a wet-niche luminaire must be at least how far below the normal water level?
- 10021A branch circuit supplies an underwater pool luminaire operating above the low-voltage contact limit. What protection is required?
- 10022For sinusoidal ac, the low-voltage contact limit used in Article 680 is how many volts RMS?