125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10013
- B: 20 ft
Explanation
All 15- and 20-ampere, single-phase, 125-volt receptacles within 20 ft of the inside walls of a pool must be GFCI protected. The zone covers outlets where people with wet hands or feet may plug in equipment.