Question 10005 of 790 · California General Electrician Exam
What is required of the main disconnecting means for an elevator?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10005
- A: A single means for each unit that opens all ungrounded supply conductors and is lockable in the open position
Explanation
Each elevator requires a single disconnecting means that opens all ungrounded main power supply conductors, is lockable open, and is located within sight of the motor controller. It must not open the car lighting circuit.