Question 9024 of 1003 · California General Electrician Exam
Where must a sealing fitting be installed in each conduit entering or leaving a fuel dispenser?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9024
- C: As the first fitting after the conduit emerges from the earth or concrete
Explanation
Each conduit run entering or leaving a dispenser requires a listed seal, which must be the first fitting after the conduit emerges from the earth or concrete. This prevents vapors from traveling through the raceway toward other equipment.
More questions: Special Occupancies
- 9025Beneath a classified area at a motor fuel dispensing facility, PVC conduit is permitted underground when buried with at least what cover, with threaded RMC or IMC used for the last section before emerging?
- 9026In a major repair garage for gasoline vehicles without the specified mechanical ventilation, how is the floor area up to 18 in above the floor classified?
- 9027The interior of a spray booth used for applying flammable paint is classified as which location?
- 9028In an aircraft hangar, the area up to 18 in above the hangar floor is classified as which location?
- 9029In health care facilities, a patient care space where failure of equipment or the electrical system is likely to cause major injury or death is which category?
- 9030A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?