Question 9030 of 790 · California General Electrician Exam
A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9030
- C: Category 2
Explanation
Category 2 is the general care space, such as inpatient bedrooms and examination rooms where failure could lead to minor injury. Category 1 is critical care, while Category 3 and Category 4 are basic care and support spaces.
More questions: Special Occupancies
- 9031Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?
- 9035The essential electrical system of a hospital is divided into which branches?
- 9036Article 518 for assembly occupancies applies to buildings or portions of buildings designed for the gathering of how many persons or more?
- 9038At a carnival, overhead conductors must maintain what minimum horizontal clearance from amusement rides and attractions?
- 9039At a carnival, circus, or fair, 125-volt, single-phase, 15- and 20-ampere receptacles used by personnel or readily accessible to the public require what protection?
- 9047Every RV site with an electrical supply in an RV park must be equipped with at least which receptacle?