Question 7062 of 790 · California General Electrician Exam
A 480Y/277 volt panelboard faces a concrete wall across the working space (Condition 2). What is the minimum working space depth?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7062
- B: 3 1/2 ft
Explanation
At 277 volts to ground the 151 to 600 volt column applies. Concrete is considered grounded, which makes it Condition 2, and Table 110.26(A)(1) requires 3 1/2 ft.