What is the minimum headroom of the working space for service equipment and panelboards rated 1000 volts or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7065
- D: 6 1/2 ft or the height of the equipment, whichever is greater
Explanation
Section 110.26(A)(3) requires the working space to be clear from the floor to a height of 6 1/2 ft or the height of the equipment, whichever is greater. Smaller existing dwelling services may have exceptions.