A fixed storage water heater holds 50 gallons. What is the minimum branch-circuit rating based on the nameplate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7048
- C: 125 percent of the nameplate rating
Explanation
Section 422.13 treats a fixed storage water heater of 120 gallons or less as a continuous load. The branch-circuit rating must therefore be at least 125 percent of the nameplate rating.