Question 7051 of 790 · California General Electrician Exam
What cord length is permitted for a cord-and-plug connected kitchen waste disposer?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7051
- D: 18 in to 36 in
Explanation
Section 422.16(B)(1) requires the cord for an in-sink waste disposer to be at least 18 in and not over 36 in long. The receptacle must be located to avoid physical damage to the cord.
More questions: Equipment, Devices and Luminaires
- 7052A permanently connected appliance is rated 250 VA. What may serve as its disconnecting means?
- 7053A permanently connected appliance rated above 300 VA is not within sight of its branch-circuit breaker. What is required?
- 7056What does Article 424 require for fixed electric space-heating equipment?
- 7058Which use of flexible cord is not permitted?
- 7059A flexible cord is run from one room to another through a hole in the wall. Is this permitted?
- 7060How must a flexible cord be connected so that tension is not transmitted to joints or terminal screws?