Question 7006 of 1003 · California General Electrician Exam
A receptacle is installed under a roofed open porch where it is protected from beating rain (a damp location). What cover is the minimum requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7006
- D: A cover that is weatherproof when closed with no plug inserted
Explanation
Section 406.9(A) allows a receptacle in a damp location to have an enclosure that is weatherproof when the receptacle cover is closed and no plug is inserted. The in-use requirement applies to wet locations under 406.9(B). The receptacle itself must still be weather resistant.