A two-wire receptacle circuit has no equipment grounding conductor. Which replacement is permitted without adding a grounding conductor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7008
- C: A GFCI receptacle marked No Equipment Ground
Explanation
Section 406.4(D)(2) (406.12(D) in NEC 2026) allows a nongrounding receptacle, a GFCI-type receptacle, or a grounding-type receptacle supplied through a GFCI where no grounding means exists. A GFCI receptacle used this way must be marked No Equipment Ground. Jumpering the ground terminal to the neutral is never allowed.