Question 6060 of 925 · California General Electrician Exam
Under NEC 2020 and 2023, what is the minimum size conductor generally permitted for branch circuit wiring in copper?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6060
- D: 14 AWG
Explanation
The general minimum conductor size is 14 AWG copper and 12 AWG aluminum or copper-clad aluminum, with exceptions for items like fixture wire and control circuits. In NEC 2023 this is 310.3(A), and the 2020 edition carries the same rule in Article 310. NEC 2026 lowered the copper minimum, which is why this question is limited to 2020 and 2023.
More questions: Wiring Methods, Conductors and Boxes
- 6061Conductors of a circuit rated 600 V and a circuit rated 120 V may occupy the same raceway only if
- 6062Why must all conductors of a circuit, including the neutral and EGC, be in the same metal raceway?
- 6063Which use of a flexible cord is prohibited?
- 6066Which location permits Type NM cable?
- 6067In an attic reached only by a scuttle hole, NM cable run across the top of joists must be protected by guard strips within what distance of the scuttle hole?
- 6068In an unfinished basement, NM cable run at angles to joists must be run through bored holes or on running boards if it is smaller than