Question 5022 of 790 · California General Electrician Exam
A service has three parallel sets of 400 kcmil copper per phase. What is the minimum copper GEC to building steel?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5022
- B: 3/0 AWG
Explanation
The equivalent area is 3 x 400 = 1200 kcmil, which exceeds 1100 kcmil. Table 250.66 requires a 3/0 copper GEC for copper service conductors over 1100 kcmil.
More questions: Grounding and Bonding
- 5023How must an 8 AWG copper grounding electrode conductor be installed?
- 5024When does a 4 AWG copper grounding electrode conductor require protection?
- 5025Under NEC 2020 and 2023, other than at busbars, a grounding electrode conductor may be spliced only by
- 5027A ferrous metal raceway that encloses a grounding electrode conductor must be
- 5030At the service, the main bonding jumper connects
- 5031What is the minimum size copper main bonding jumper for a service with 4/0 AWG copper ungrounded conductors?