A service has 4/0 AWG copper ungrounded conductors. What is the minimum copper GEC to the building steel electrode?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5019
- C: 2 AWG
Explanation
Copper service conductors over 3/0 through 350 kcmil require at least a 2 AWG copper GEC under Table 250.66. 4/0 falls in that range.
More questions: Grounding and Bonding
- 5020A service has 500 kcmil copper ungrounded conductors. What is the minimum copper GEC to a water pipe electrode?
- 5021A service has two parallel sets of 3/0 AWG copper (about 168 kcmil each). What is the minimum copper GEC to a water pipe electrode?
- 5022A service has three parallel sets of 400 kcmil copper per phase. What is the minimum copper GEC to building steel?
- 5023How must an 8 AWG copper grounding electrode conductor be installed?
- 5024When does a 4 AWG copper grounding electrode conductor require protection?
- 5025Under NEC 2020 and 2023, other than at busbars, a grounding electrode conductor may be spliced only by