The portion of a grounding electrode conductor that is the sole connection to one or more ground rods is not required to be larger than
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5015
- C: 6 AWG copper
Explanation
A GEC run only to rod, pipe, or plate electrodes need not be larger than 6 AWG copper or 4 AWG aluminum, regardless of the service size. See 250.66(A).