Question 4075 of 790 · California General Electrician Exam
A dwelling foyer that is not part of a hallway requires a receptacle on each wall space 3 ft or more wide when the foyer area is greater than what size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4075
- D: 60 sq ft
Explanation
210.52(I) requires a receptacle on each wall space 3 ft or more in width in foyers with an area greater than 60 sq ft. Doorways, door side windows that extend to the floor and similar openings do not count as wall space.
More questions: Branch Circuits, GFCI and AFCI