Question 4079 of 790 · California General Electrician Exam
A hotel guest suite includes permanent provisions for cooking. Which receptacle rules apply to the suite?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4079
- A: The dwelling unit receptacle rules of 210.52
Explanation
210.60(A) requires guest rooms and guest suites with permanent provisions for cooking to have receptacle outlets installed in accordance with all applicable rules of 210.52. This includes kitchen countertop receptacles and small-appliance circuits.
More questions: Branch Circuits, GFCI and AFCI
- 4080A 20-ampere branch circuit supplies two or more receptacles. Which receptacle ratings are permitted?
- 4081A single receptacle is installed on an individual 20-ampere branch circuit. What is the minimum rating of the receptacle?
- 4082What is the maximum cord-and-plug load permitted on a 20-ampere receptacle supplied by a 20-ampere branch circuit with multiple outlets?
- 4084On a 20-ampere branch circuit, what is the maximum rating of a single cord-and-plug-connected utilization equipment not fastened in place?
- 4085A 20-ampere branch circuit supplies lighting units and also fastened-in-place utilization equipment. What is the maximum total rating of the fastened-in-place equipment?
- 4086Which loads are 40-ampere and 50-ampere branch circuits permitted to supply in any occupancy?