Question 4027 of 925 · California General Electrician Exam
Under the NEC 2023 and 2026, a 50-ampere, 120/240-volt range receptacle is installed in a dwelling kitchen more than 6 ft from the sink. Is GFCI protection required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4027
- C: Yes, kitchen receptacles and electric ranges are now covered
Explanation
From the 2023 edition, all dwelling kitchen receptacles up to 250 volts are covered by 210.8(A), and 210.8(D) lists electric ranges among the appliances needing GFCI. The range receptacle therefore needs GFCI protection, usually a 2-pole GFCI breaker.
More questions: Branch Circuits, GFCI and AFCI
- 4028Which of the following appliances requires GFCI protection for its outlet regardless of the occupancy?
- 4029Under the NEC 2023, the GFCI list for specific appliances in 210.8(D) applies to outlets on branch circuits rated 150 volts or less to ground and at what maximum current?
- 4030Under the NEC 2020 and 2023, dwelling unit outdoor outlets on single-phase branch circuits rated 150 volts or less to ground require GFCI protection up to what branch circuit rating?
- 4033Under the 2023 NEC, an exception to 210.8(F) states GFCI protection is not required for listed HVAC equipment until what date?
- 4038In a dwelling unit, which of the following locations requires AFCI protection for 120-volt, 15- and 20-ampere branch circuits supplying outlets?
- 4040Which of the following dwelling unit circuits requires AFCI protection?