Question 4029 of 925 · California General Electrician Exam
Under the NEC 2023, the GFCI list for specific appliances in 210.8(D) applies to outlets on branch circuits rated 150 volts or less to ground and at what maximum current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4029
- B: 60 amperes or less
Explanation
The 2023 edition moved the appliance GFCI list from 422.5 into 210.8(D) and applies it to single-phase or three-phase outlets rated 150 volts or less to ground and 60 amperes or less. Items such as ranges, dryers and microwave ovens were added at the same time.
More questions: Branch Circuits, GFCI and AFCI
- 4030Under the NEC 2020 and 2023, dwelling unit outdoor outlets on single-phase branch circuits rated 150 volts or less to ground require GFCI protection up to what branch circuit rating?
- 4033Under the 2023 NEC, an exception to 210.8(F) states GFCI protection is not required for listed HVAC equipment until what date?
- 4038In a dwelling unit, which of the following locations requires AFCI protection for 120-volt, 15- and 20-ampere branch circuits supplying outlets?
- 4040Which of the following dwelling unit circuits requires AFCI protection?
- 4041In a college dormitory unit, 120-volt, 15- and 20-ampere branch circuits supplying outlets in bedrooms and living rooms require which protection?