Under the high-bay manufacturing tap rule, what is the maximum total length of the feeder tap?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3049
- B: 100 ft
Explanation
In high-bay manufacturing buildings over 35 ft high at the walls, with qualified maintenance, taps may be up to 100 ft in total with not more than 25 ft horizontal. The tap ampacity must be at least one-third of the feeder OCPD rating. See 240.21(B)(4).