A feeder conductor has an ampacity of 115 A and does not supply receptacles for portable loads. What is the largest standard OCPD permitted under the next size up rule?

Exactly one answer is correct.

Show solution

Correct answer to question 3025

  • A: 125 A

Explanation

Where the ampacity does not match a standard rating, the next higher standard rating may be used if it does not exceed 800 A. 115 A is not standard, so 125 A is the next higher rating. See 240.4(B) and 240.6(A).