Question 2006 of 790 · California General Electrician Exam
Overhead service conductors run beside a window that is designed to be opened. What minimum horizontal clearance from the window is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- B: 3 ft
Explanation
Service conductors must be kept at least 3 ft from windows designed to be opened, doors, porches, balconies, ladders, stairs and fire escapes. Conductors run above the top level of a window are exempt. See 230.9(A).
More questions: Services and Service Equipment
- 2007Since the 2020 edition, what is required for all services supplying dwelling units?
- 2008Which statement about overhead service conductors and building openings is correct?
- 2010Under the 2023 and 2026 NEC, a one-family dwelling is supplied by a feeder from a service on a pole. What is required for this dwelling?
- 2012In general, how many services may supply a single building or structure?
- 2014What is the minimum size copper conductor permitted for an overhead service drop, other than for limited loads?
- 2016Where must a service head generally be located in relation to the point of attachment of the service drop?