Question 2010 of 790 · California General Electrician Exam
Under the 2023 and 2026 NEC, a one-family dwelling is supplied by a feeder from a service on a pole. What is required for this dwelling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2010
- C: An outdoor emergency disconnect for the feeder
Explanation
Section 225.41, added in 2023, requires an emergency disconnecting means in a readily accessible outdoor location for one- and two-family dwellings supplied by feeders. An existing outdoor feeder disconnect complying with the rule can serve this purpose.