Under the 2023 NEC, a listed disconnect switch installed on the supply side of each service disconnect serves as the dwelling emergency disconnect. How must it be marked?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2003
- C: EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT
Explanation
Where the emergency disconnect is a separate device ahead of the service disconnects, it must be suitable for service equipment and marked EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT. If the service disconnects themselves serve the purpose, they are marked EMERGENCY DISCONNECT, SERVICE DISCONNECT. See 230.85.