Question 13104 of 790 · California General Electrician Exam
A single-phase transformer steps 480 volts down to 120 volts. If the primary current is 10 A, what is the secondary current (ignoring losses)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13104
- D: 40 A
Explanation
The turns ratio is 480 / 120 = 4 to 1, and current changes inversely with voltage: 10 x 4 = 40 A. Dividing by the ratio (2.5 A) applies the voltage relationship to current.
More questions: Electrical Calculations
- 13105A transformer has a turns ratio of 20 to 1 and a primary voltage of 2,400 volts. What is the secondary voltage?
- 13106A balanced three-phase load draws 150 A per phase at 208 volts. What is the minimum transformer kVA required?
- 13107A transformer delivers 48.5 kW to its load while its input is 50 kW. What is its efficiency?
- 13108A 15 kVA, single-phase transformer with a 240 volt primary is protected on the primary side only. Which statement about its primary current is correct?
- 13109A branch circuit supplies a 36 A continuous load and nothing else. What is the minimum overcurrent device rating?
- 13110A 40 A continuous load is supplied with THWN copper conductors terminating on 75 °C rated equipment. What is the minimum conductor size?