Question 13094 of 790 · California General Electrician Exam
A feeder supplies three 460 volt, three-phase motors with table full-load currents of 14 A, 21 A and 34 A. What is the minimum feeder conductor ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13094
- B: 77.5 A
Explanation
Feeder conductors must carry 125 % of the largest motor plus the sum of the others: 34 x 1.25 + 14 + 21 = 77.5 A. Adding them without the 25 % (69 A) or applying 125 % to all (86.3 A) are the common mistakes.
More questions: Electrical Calculations
- 13095A 1 hp, 115 volt, single-phase motor has a table full-load current of 16 A. What minimum branch-circuit conductor ampacity is required?
- 13096A feeder supplies three 460 volt motors: 25 hp (34 A) protected by a 90 A inverse time breaker, 15 hp (21 A) and 10 hp (14 A). What is the maximum rating of the feeder overcurrent device?
- 13097What is the Table 430.250 full-load current for a 50 hp, 230 volt, three-phase induction motor?
- 13098A 7.5 hp, 460 volt, three-phase motor has a table full-load current of 11 A. What minimum branch-circuit conductor ampacity is required?
- 13099Why does the full-load current from Table 430.250, rather than the motor nameplate current, determine motor branch-circuit conductor ampacity for a general-purpose motor?
- 13100A 25 kVA single-phase transformer has a 480 volt primary and a 240 volt secondary. What are the full-load primary and secondary currents?