Question 13096 of 790 · California General Electrician Exam

A feeder supplies three 460 volt motors: 25 hp (34 A) protected by a 90 A inverse time breaker, 15 hp (21 A) and 10 hp (14 A). What is the maximum rating of the feeder overcurrent device?

Exactly one answer is correct.

Show solution

Correct answer to question 13096

  • D: 125 A

Explanation

The feeder device may not exceed the largest branch-circuit short-circuit and ground-fault device plus the sum of the other motors' full-load currents: 90 + 21 + 14 = 125 A. Since 125 A is a standard size it may be used, and rounding up to 150 A is not permitted for feeders.