Question 13051 of 790 · California General Electrician Exam

Four current-carrying 3/0 AWG THWN-2 copper conductors are installed in a raceway where the ambient is 50 °C. What is the derated ampacity from the 90 °C column?

Exactly one answer is correct.

Show solution

Correct answer to question 13051

  • C: 147.6 A

Explanation

The 90 °C ampacity of 3/0 copper is 225 A; the 46 to 50 °C factor is 0.82 and four conductors require 80 %: 225 x 0.82 x 0.80 = 147.6 A. Forgetting the 80 % adjustment gives 184.5 A, and forgetting the temperature correction gives 180 A.

Next to question ›