Question 13054 of 790 · California General Electrician Exam
A raceway contains two 3-phase, 4-wire wye circuits, and the loads are mainly electronic (nonlinear), so the neutrals count as current-carrying. Equipment grounding conductors are also present. What adjustment factor applies?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13054
- B: 70 %
Explanation
Each circuit has three phase conductors plus a neutral that must be counted, giving 8 current-carrying conductors, and 7 to 9 conductors call for 70 %. Equipment grounding conductors are never counted.
More questions: Electrical Calculations
- 13055A raceway holds three 120 volt, 2-wire branch circuits, each with its own neutral, plus one equipment grounding conductor per circuit. How many current-carrying conductors are counted for adjustment?
- 13056A raceway contains three 120/240 volt, single-phase 3-wire multiwire circuits. The neutrals carry only unbalanced current. What adjustment factor applies to the conductors?
- 13057What is the allowable ampacity of 4/0 AWG XHHW aluminum conductors in the 75 °C column at 30 °C ambient with not more than three current-carrying conductors?
- 1305812 AWG copper UF cable (60 °C rated) is installed where the ambient temperature is 40 °C. What is its corrected ampacity?
- 13059A 50 A noncontinuous load is supplied by one of six current-carrying THHN copper conductors in a raceway at 30 °C. Terminations are rated 75 °C. What is the smallest conductor size permitted?
- 13060Twenty current-carrying 12 AWG THHN copper conductors are in one raceway at 30 °C ambient. What is the adjusted ampacity based on the 90 °C column?