A 120 volt, 20 A load is 150 feet from the panel. What is the smallest copper conductor that keeps voltage drop at or below 3 %?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13045
- A: 6 AWG
Explanation
Allowed drop is 3.6 V, so CM = 2 x 12.9 x 20 x 150 / 3.6 = 21,500 circular mils. 8 AWG has only 16,510 circular mils, so 6 AWG (26,240) is the minimum; 12 AWG would be sized for ampacity alone.