Egress lighting required by a building code to illuminate exit paths during a power outage is part of which system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11016
- C: Emergency system (Article 700)
Explanation
Illumination for safe exiting and exit signs are classic emergency system loads. They must be restored within 10 seconds.
More questions: Emergency, Limited Energy and Communications
- 11017A code-required system supplies sewage disposal pumps and smoke removal equipment during outages, with less urgency than egress lighting. Which system is this?
- 11018A portable generator is connected to a dwelling's premises wiring as an optional standby source. What is required?
- 11019In NEC 2020 and 2023, which article covers energy management systems?
- 11023May Class 2 conductors be installed in the same raceway as power conductors?
- 11032What identification is required on the disconnecting means for a fire alarm branch circuit?
- 11033Which power-limited fire alarm cable type is suitable for installation in plenums?