A portable generator is connected to a dwelling's premises wiring as an optional standby source. What is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11018
- D: Transfer equipment that prevents inadvertent interconnection of normal and standby sources
Explanation
Optional standby systems connected to premises wiring require transfer equipment designed to prevent inadvertent interconnection of the normal and alternate sources. A back-feed cord is dangerous and not permitted.