Question 11008 of 925 · California General Electrician Exam
Battery-powered emergency lighting unit equipment must supply the full lamp load for at least how long?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11008
- C: 1.5 hours
Explanation
Unit equipment batteries must be able to supply the lighting load for at least 1.5 hours, at not less than 87.5 percent of nominal voltage. This matches typical egress lighting duration requirements.
More questions: Emergency, Limited Energy and Communications
- 11009How must emergency lighting systems be designed with respect to lamp failure?
- 11010Where on-site emergency power sources are installed, a sign must be placed where?
- 11011Which record must be kept for an emergency system?
- 11013In assembly occupancies for more than 1000 persons or buildings above 75 ft in height, emergency feeder circuit wiring must have what protection?
- 11014In NEC 2020 and 2023, which article covers fire-resistive cable systems?
- 11016Egress lighting required by a building code to illuminate exit paths during a power outage is part of which system?