Question 1050 of 790 · California General Electrician Exam
On a balanced three-phase, four-wire wye system serving only linear resistive loads, the neutral current is:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1050
- C: Approximately zero
Explanation
With equal loads on all phases and no harmonics, the three phase currents cancel at the neutral point because they are 120 degrees apart. Unbalance or nonlinear loads cause neutral current.
More questions: Definitions, Theory and Plans
- 1051On a wye system serving many computers and LED drivers, which harmonics add together in the neutral instead of canceling?
- 1052Which expression gives the true power of a balanced three-phase load?
- 1053How is the rotation of a three-phase induction motor reversed?
- 1054What is the synchronous speed of a 4-pole induction motor on a 60 Hz supply?
- 1055The difference between the synchronous speed of the rotating field and the actual rotor speed of an induction motor is called:
- 1056A transformer has 1,000 turns on the primary and 100 turns on the secondary. If 480 volts is applied to the primary, the secondary voltage is: