On a 240/120-volt three-phase, four-wire delta system with a center-tapped winding, the high leg measures approximately how many volts to the neutral?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1049
- A: 208 volts
Explanation
Two phases measure 120 V to the center-tap neutral, but the third (high or wild) leg measures about 208 V to neutral. It must be identified so it is not used for 120-volt loads.