Question 10075 of 1003 · California General Electrician Exam
An EVSE capable of bidirectional power flow that is used as an optional standby or interactive source must meet which requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10075
- A: It must be listed for the purpose and installed per the relevant power source articles
Explanation
EVSE that exports power from the vehicle to premises wiring must be listed and marked for that function, and the installation must comply with Articles 702, 705, or 706 as applicable. Proper listing ensures safe interconnection.
More questions: Special Equipment, Pools, PV and EV
- 10076The OCPD for a fire pump motor must be sized to carry what current indefinitely?
- 10077In NEC 2020 and 2023, fire pump supply conductors inside a building may be protected by encasement in at least how much concrete?
- 10079Which statement about overload protection for fire pump supply conductors is correct?
- 10080During motor starting, the voltage at the fire pump controller line terminals must not drop more than what percentage below the controller rated voltage?
- 10081A fire pump motor has a full-load current of 40 amperes and no accessory loads. What is the minimum ampacity of the supply conductors?
- 10082What is required of a fire pump disconnecting means?