Which statement about overload protection for fire pump supply conductors is correct?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10079
- C: They must not have automatic overload protection, only short-circuit and ground-fault protection
Explanation
Fire pump power circuits must not have automatic protection against overloads, except as specifically permitted. Only short-circuit and ground-fault protection are provided so the pump keeps running during a fire.