Question 10063 of 1003 · California General Electrician Exam
Article 706 applies to permanently installed energy storage systems with a capacity greater than what amount?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10063
- A: 1 kWh (3.6 MJ)
Explanation
Article 706 covers permanently installed ESS having a capacity greater than 3.6 MJ, which equals 1 kWh. Smaller storage is covered by other rules.
More questions: Special Equipment, Pools, PV and EV
- 10064What protection is required for receptacles installed for the connection of EV charging equipment?
- 10065An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
- 10066An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?
- 10067How must each outlet installed for EVSE be supplied?
- 10068Indoor EV charging equipment is listed as requiring ventilation. What does the NEC require?
- 10069In NEC 2020 and 2023, EVSE rated more than 60 amperes or more than 150 volts to ground requires a disconnecting means with which characteristics?