Question 10065 of 790 · California General Electrician Exam

An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?

Exactly one answer is correct.

Show solution

Correct answer to question 10065

  • B: 60 amperes

Explanation

EV branch circuits are sized for continuous duty, with an OCPD of not less than 125 percent of the maximum load: 48 A x 1.25 = 60 A. 60 A is a standard size.