Question 8069 of 1003 · California General Electrician Exam
A 150 kVA dry-type transformer rated over 112.5 kVA is installed indoors. Generally, where must it be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8069
- A: In a transformer room of fire-resistant construction
Explanation
Section 450.21(B) requires indoor dry-type transformers over 112.5 kVA to be installed in a transformer room of fire-resistant construction, with exceptions such as transformers with high-temperature insulation separated by barriers or distance.
More questions: Motors, HVAC, Generators and Transformers
- 8070Under what condition may a dry-type transformer be installed above a suspended ceiling?
- 8071A transformer is located out of sight of its supply disconnect. What does 450.14 require?
- 8072Oil-insulated transformers installed indoors are generally required to be installed in what?
- 8073What is the general fire resistance rating required for transformer vault walls and roofs?
- 8074Secondary conductors leave a transformer and do not exceed 10 ft in length. What may they terminate in without protection at the secondary terminals?
- 8075Capacitors rated 1000 volts or less must discharge their residual voltage to what level within what time after disconnection?