A transformer rated 1000 volts or less has both primary and secondary protection. What is the maximum primary device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8064
- D: 250 percent of rated primary current
Explanation
Table 450.3(B) allows the primary device to be rated up to 250 percent of the primary current when secondary protection is also provided. The secondary device is then normally limited to 125 percent for secondary currents of 9 A or more.