Question 7024 of 790 · California General Electrician Exam
Snap switches in a single box have more than 300 volts between adjacent devices. What is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7024
- D: Identified, securely installed barriers between the switches
Explanation
Section 404.8(B) requires identified barriers between adjacent snap switches when the voltage between exposed live parts of the devices exceeds 300 volts. Otherwise the switches must be arranged so the voltage does not exceed 300 volts.
More questions: Equipment, Devices and Luminaires
- 7027A hallway light must be controlled from three separate locations. Which combination of switches is used?
- 7028How many traveler terminals does a standard four-way switch have, not counting the grounding terminal?
- 7029In a three-way switch circuit, which terminal of the switch at the supply end connects to the incoming ungrounded conductor?
- 7030How must each circuit be identified on a panelboard circuit directory?
- 7031Which panelboard directory entry best meets the code?
- 7032The old limit of 42 overcurrent devices for lighting and appliance branch-circuit panelboards was removed in the 2008 NEC. What limits the number of devices today?